I'm updating a 1950s 2/1 900SF home in South Carolina. The electrician suggests upgrading to a 200 electrical service entry with through the roof mast and relocate existing circuits into a single EXTERIOR 40-space 200-amp panel box with a main disconnect. The panel box is currently in a corner of the kitchen and the refrigerator is pulled away from the wall to allow access to it. In the future I may put a counter there or something. Guess you could put a small shelf under it for now to make use of the space.
I don't see the problem with it, but the person who is moving into the home (a friend of mine) is freaking out over the panel box being relocated to the outside. I live in Wyoming and mine is outside so it didn't seem like a big deal to me and would give more options in an already very tiny kitchen.
What are your thoughts on location of the panel box? Thanks.
@Tina S. In CA we mainly have them outside. Back in the day, When I was young, I’m not a kid anymore but... this one day a kid went around the neighborhood turning people’s houses off for fun, so there are reasonable concerns there.
@Tina S. You do typically have to have that 3.5' clearance for code compliance, and it is a good upgrade to 200 amp if you don't have propane or natural gas running stove, and dryer. I built a house in VA once where the electrician was "saving me money" by doing a 100amp and it didn't pass the inspection. Had to wire in 200amp. I've seen people lock the panels outside and that works.
Tina, since we sold you the house I may be biased but outside is fine. Many, many houses here are outside. Behind the fridge where it currently is won’t work but 200 amp seems like too much, even with a washer-dryer. It is odd that the panel was upgraded once yet they stuck the fridge in front if it.
I can’t imagine that it’d save much but 150 amp service seems like enough.
Unless adding a third bedroom/master bath in the future is a consideration. There is room enough to do that and then you’d have 200 amp service in place.
Tina, since we sold you the house I may be biased but outside is fine. Many, many houses here are outside. Behind the fridge where it currently is won’t work but 200 amp seems like too much, even with a washer-dryer. It is odd that the panel was upgraded once yet they stuck the fridge in front if it.
I can’t imagine that it’d save much but 150 amp service seems like enough.
Unless adding a third bedroom/master bath in the future is a consideration. There is room enough to do that and then you’d have 200 amp service in place.
Maybe one more electrician’s opinion?
@Christopher Bunge. The cost difference from 150 to 200 is negligible. The availability of 150 is becoming scarcer. In my region 100/200 are the norm.
Just did a quick price/availability check on Home Depot's website. My local store has 8 200 amp load centers priced cheaper than the cheapest 150 amp one. Indoor or outdoor and up to 64 circuits. So it's not the parts cost that's a concern, just the labor. Most panels don't have enough wire to be moved 2 feet further away. Running new wire is expensive. I'd find a way to move the refrigerator if that's possible.
If you use a licensed contractor, get permitted, and have it inspected your insurance company will be much happier.They'll have 2 people with deeper pockets to go after when someone gets fried playing with the panel while standing in water. LOL
Outdoor panels were the standard down here in Florida until about 15 years ago.
I saw an outside panel once on a flipping show and thought that's like a unicorn being that I've never seen one in person, I had no idea this was a common thing is some areas.
@Tina S. From a security standpoint, it seems like it should be on the inside of the home. Having it outside means that ANYONE can cut the power off to the home.
@Christopher Bunge Hi Chris!I talked to the electrician about the 200 amp because my father in law thought the same thing. But the price difference was so minuscule that it made sense to go with the 200.
I'm excited about the progress the house is making and you should come by and check it out after the new roof is put on hopefully next month.
I am a lineman by trade and work on or around electrical panels on near a daily basis. The outdoor panel configuration you’re describing is actually the most common and very safe when professionally installed. Not sure why your friend has an issue with it but rest assured there’s nothing wrong with it.
I've always had mine inside the garage or I'm a basement space. Last thing I want to be doing is standing outside in a rainstorm trying to flip a breaker.
I am a lineman by trade and work on or around electrical panels on near a daily basis. The outdoor panel configuration you’re describing is actually the most common and very safe when professionally installed. Not sure why your friend has an issue with it but rest assured there’s nothing wrong with it.
Tina, I know you are trying to do what's right for your friend/tenant but I am willing to bet Tim's experience with breaker boxes against hers. ;)
To be honest, in New England it is not common to see them outside. You may see a large disconnect on the exterior near the meters, but the panels are typically located inside of the house. I'd recommend just making sure it installed in accordance with electrical code.