Skip to content
×
Pro Members Get
Full Access!
Get off the sidelines and take action in real estate investing with BiggerPockets Pro. Our comprehensive suite of tools and resources minimize mistakes, support informed decisions, and propel you to success.
Advanced networking features
Market and Deal Finder tools
Property analysis calculators
Landlord Command Center
ANNUAL Save 16%
$32.50 /mo
$390 billed annualy
MONTHLY
$39 /mo
billed monthly
7 day free trial. Cancel anytime

Let's keep in touch

Subscribe to our newsletter for timely insights and actionable tips on your real estate journey.

By signing up, you indicate that you agree to the BiggerPockets Terms & Conditions
×
Take Your Forum Experience
to the Next Level
Create a free account and join over 3 million investors sharing
their journeys and helping each other succeed.
Use your real name
By signing up, you indicate that you agree to the BiggerPockets Terms & Conditions.
Already a member?  Login here
Followed Discussions Followed Categories Followed People Followed Locations
Rehabbing & House Flipping
All Forum Categories
Followed Discussions
Followed Categories
Followed People
Followed Locations
Market News & Data
General Info
Real Estate Strategies
Landlording & Rental Properties
Real Estate Professionals
Financial, Tax, & Legal
Real Estate Classifieds
Reviews & Feedback

Updated over 12 years ago on . Most recent reply

User Stats

2
Posts
2
Votes
Ed Melo
  • Glenmoore, PA
2
Votes |
2
Posts

3 hole outlet on ungrounded line

Ed Melo
  • Glenmoore, PA
Posted

I have seen some older houses where some of the outlets have been replaced with 3 hole outlets although the line going to them do not have a ground wire.

Is the only good solution to this problem replacement of the wiring?

Would you replace ALL the ungrounded wiring ? I'm sure this could be expensive but is it safe to leave the ungrounded wiring in place?

Most Popular Reply

User Stats

22,059
Posts
14,128
Votes
Jon Holdman#3 Real Estate Deal Analysis & Advice Contributor
  • Rental Property Investor
  • Mercer Island, WA
14,128
Votes |
22,059
Posts
Jon Holdman#3 Real Estate Deal Analysis & Advice Contributor
  • Rental Property Investor
  • Mercer Island, WA
ModeratorReplied

The ground bar and the neutral bar should be tied together in the main service panel, and should be connected both to the neutral service wire from the electric company and to an earth ground. You're right, Ryan, that its just a longer route to the same place. The point is to create a separate route. In a subpanel, such as in a garage, the ground and neutral busbars would not be tied together. Rather, each should have a separate connection back to the main service panel.